BACnet Client Station Error

Discussion of configuring and troubleshooting communication to PLC's or other devices using iX Developer.
Post Reply
johnkat
Posts: 3
Joined: Fri Apr 10, 2020 12:39 am

BACnet Client Station Error

Post by johnkat »

Hello,

I am using a X2 Base 7 to read data from a BACnet scada system.
I have done multiple tests and if I add up to 12 tags everything works fine.
However when I add 1 more tag (13 total) an error appears (picture).

It is important to mention that the error is irrelevant to the tag. Because if I try to get the 13th tag alone it works fine. The problem seems to be related with the "maximum number of tags" which seems to be 12 at the moment.

Any help is more than welcome
Thank you

Pictures
1) Reading succesfully 12 Tags
3) TAG configuration 13 Tags
2) Trying to read 13 Tags
Attachments
Screenshot 2020-10-05 110739.png
Screenshot 2020-10-05 110739.png (4.5 KiB) Viewed 6392 times
Screenshot 2020-10-05 110237.png
Screenshot 2020-10-05 110237.png (129.69 KiB) Viewed 6393 times
Screenshot 2020-10-05 110029.png
Screenshot 2020-10-05 110029.png (5.07 KiB) Viewed 6393 times

Post Reply