Hi,
after restarting HMI, screen stuck in start-up screen saying 'Verifying storage 'Database''. Did someone have this situation and how to resolve it. (see attached picture)
Thanks
Verifying storage 'Database'
Verifying storage 'Database'
- Attachments
-
- IMG-20200509-WA0003.jpg (71.13 KiB) Viewed 10213 times
Re: Verifying storage 'Database'
Hello Lukas0204,
Have you tried rebuilding the project (Project > Rebuild) before transferring to the panel? The Rebuild MAY clean up some of the database issues automatically for you.
Have you tried rebuilding the project (Project > Rebuild) before transferring to the panel? The Rebuild MAY clean up some of the database issues automatically for you.
Re: Verifying storage 'Database'
Hi,prichlin wrote:Hello Lukas0204,
Have you tried rebuilding the project (Project > Rebuild) before transferring to the panel? The Rebuild MAY clean up some of the database issues automatically for you.
yes, each time before downloading, I rebuild the project.
Just to update situation:
Today I was on a site to see a problem and each time when I reset HMI (power cycle), HMI stayed for around 20 minutes in screen 'Verifying storage 'Database' before going in normal run. Than I made button 'Database Cleanup' and this solved a problem. Also, I saw in diagnostic that FlashDrive after Database cleanup was using only 1% of its memory. Before that was using 23% but it's hard to believe that could cause any kind of HMI overload?!
Also, to be more detailed:
- Datalogger contains 55 tags; log interval = 5 sec, max log rows: 1296000
- 42 screens
- HMI is in function for almost a year
- X2 PRO 12